How much more continuous load can be added to a 400-ampere service already utilizing 58 kilovolt-amperes of load?

Maximize your success on the Electric Vehicle Charging System Test. Sharpen your skills with multiple choice questions, insightful hints, and detailed explanations. Prepare effectively for your exam today!

To determine how much more continuous load can be added to a 400-ampere service already utilizing 58 kilovolt-amperes (kVA) of load, you need to first understand the capability of the service in terms of its voltage and total load potential.

A 400-ampere service can handle a specific maximum load based on the system voltage. For example, if we're dealing with a common service voltage such as 240 volts, the maximum load can be calculated using the formula:

Load (in kVA) = Voltage × Current (in Amperes) ÷ 1000.

At 240 volts for a 400-ampere service, the maximum load would be:

Load = 240 V × 400 A ÷ 1000 = 96 kVA.

Since the service is already using 58 kVA of load, the remaining capacity can be calculated:

Remaining Load Capacity = Maximum Load - Existing Load

Remaining Load Capacity = 96 kVA - 58 kVA = 38 kVA.

To convert the remaining capacity into volt-amperes (VA), multiply by 1,000 (since 1 kVA = 1000 VA):

Remaining Load Capacity = 38 kVA